I've seen this only once, and it was with closed cell foam, but I've heard of it happening with open cell foam, too. I don't know the details, but I've heard it could result from a bad batch of chemicals, improper mixing, or too high a temperature. Whatever the cause, it's not a good thing. The photo below shows how the spray foam pulled away from the studs. A little bit of uninsulated area like that adds up to a lot of heat loss/gain when the whole house has that problem, as it did here. Spray Coating Services
Jennifer, I'm not an expert on the health effects of closed cell foam. A lot of people live in houses with closed cell foam and have no health problems from it, at least not short-term, acute problems. I do know of one person who had it removed from her crawl space because she was convinced it caused her dog to get sick, but I know only what she told me.   Spray Coating
I am building a house in Central Texas (Caldwell). Several builders are cautious about using foam insulation and/or a closed attic. I would like to use both. Here in Texas, heat and humidity (except for the past few years of drought) are a continuing problem. Which type of foam would be the best to use in our home, where should the vapor barrier be or should be use one at all, if we are using fans in the exterior walls to supply fresh air to the house, do we need a vented attic or will it cause more problems than it solve? I have printed out your article and the blogs to give to my contractors and architect, but I would really appreciate your comments on the products being used in my part of the US. 
RE: my June 12 post...We went ahead and had the attic sprayed with a Soy-based product. Stayed in a hotel for 3 nites. Still smelled a little bad but that's gone away over time. I'm very glad we didn't use the other foam as even that much outgassing of a petrochemical could have sent my wife to the hospital. Unfortunately, the spray crew didn't speak English(at least not to me) and were kinda lazy, so they ended up spraying over some can fixtures from the kitchen below that were not insulation-contact rated. So I hired an electrician to come out, pull down the cans, pull out what he thought was an appropriate amount of foam to create a big enough air space and then re-install the cans. I billed the firm for the electrician plus an extra night we had to stay in the hotel and they paid, no questions asked. Guess they knew they had screwed up.   Spray Coating Services
Prodex reflects 97% of the radiant energy (primary source of heat flow) that strikes it - Which also protects your animals from Black Globe Effect. Prodex also reflects back the heat inside your steel building. Each unit of radiant heat energy that is reflected away from your barn in the summer, and each unit that is reflected back during the winter, means less operation of your heating and air conditioning system - Less wear and tear on your equipment - Less money you pay in utility costs.
When do you need an ignition barrier? According to the IRC and IBC, an attic or crawl space needs an ignition barrier over the spray foam if the space can be accessed but will not be used for storage or auxiliary living space. You don't need an ignition barrier if the space cannot be accessed without cutting into it, if it is not connected to other spaces, and if it does not communicate with other spaces. Spray Coating Services
Manufacturers who mass-produce wood products use automated spray systems, allowing them to paint materials at a very high rate with a minimum of personnel. Automated spray systems usually incorporate a paint-saving system which recovers paint not applied to the products. Commonly, linear spray systems are for products which are lying flat on a conveyor belt and then fed into a linear spray system, where automated spray guns are stationed above. When the material is directly below the guns, the guns begin to paint the material. Materials consist of lineal parts usually less than 12 inches (30 cm) wide, such as window frames, wood moulding, baseboard, casing, trim stock, and any other material that is simple in design. These machines are commonly used to apply stain, sealer, and lacquer. They can apply water- or solvent-based coatings. In recent years ultraviolet-cured coatings have become commonplace in profile finishing, and there are machines particularly suited to this type of coating. Insulation Spray Coating

Surface Preparation (Residential & Commercial): Pressure wash when possible using pure water. Be sure the surface is clean and completely dry before the application of the coating. Read all label instructions before beginning. Surface must be in savable condition, clean and dry, and should have proper drainage. Always run a test patch first in an inconspicuous area, to ensure that proper adhesion and drying occurs and the product works to your satisfaction. Apply Ames® Peel & Stick™ adhesive seam tape and tape on all badly deteriorated fasteners, rubber washers, joints, seams and around vents. Do not use any soaps or detergents to clean the surface. Spray Coating
Car was washed with Carpro reset and wiped down with Griots garage paint prep to ensure a clean surface for first application of CMX. Week one CMX had a nice gloss with small tight beads after getting rained on (typical Si02 protection). Week two the beads were large and flat (low contact angle) so product was on it's way out. Week three the water was sheeting with no beading at all. That's complete failure in three weeks. Also I didn't like the white crystals that developed in the bottle. I'm concerned that if I used the product again that I'd mar my Audi's Mythos black paint. My car is parked outside driven only about 50 miles per week and is washed weekly with Megs gold class car wash. . Won't apply it again. Moving on.... Coating Services
Health monitoring: In order to avoid development of illnesses associated with exposure to isocyanates, health authorities recommend that people who use spray paint products that contain the substance provide a urine sample after a work shift at least once a year, with high frequencies in first few months on the job. A urine sample with ascertain levels of exposure, not the presence of disease associated with harmful chemicals.

In addition, it's difficult for an inexperienced installer to evenly spread the insulation foam over a surface. Miissing spots can leave holes and gaps for cold air to get through. Proceed with this project yourself only if you're doing a small insulation project -- such as installing foam in a crawl space or around your plumbing. Leave larger projects like the attic, basement or garage to the professional insulation contractors. Insulation professionals have the tools, equipment and background knowledge necessary. Moreover, they know how to accurately price insulation, whereas you could inaccurately budget for a DIY project and end up paying significantly more. Don't take the medical, physical or financial risks that come with pursuing this as a DIY project unless you're absolutely certain you have the skills.
There are exceptions to the thermal barrier rules. If the spray foam insulation is used as roofing or covered by concrete whichis, at least, an inch thick, then thermal barriers are not necessary. Additionally, you do not have to use a thermal barrier if the spray foam insulation is used on the interior of sill plates and rim joists, so long as the spray foam is 3 1/4 inches or less. Thermal barriers are also not necessary if the spray foam insulation is used in an attic or crawl space, as long as they are not used for storage or as living areas. In attics and crawl spaces where thermal barriers are not required, the use of ignition barriers is necessary.
Condensation - It can seem like a tropical rain forest inside an unprotected metal building. It's worse on those days where there is a greater contrast between temperatures at night vs. day. The morning sun hitting the cool sheeting will create a drip. A temperature difference between outside and inside your building creates condensation - Similar to what happens when you leave a cold can of beer outside on a hot day.  Insulation Spray Coating
I applied the Gaco 100% Silicone Roof coating to a slightly-sloped, metal porch roof.  My leaks have stopped, and it looks like they are gone for good.  I followed the instructions, and it appears the product made a perfect bond to the roof.  What a terrific product!  I'm glad I made this purchase, and that I didn't settle for a cheap, metal coating from the local outlet store. Coating Services

Whether or not an intumescent coating, or even a thermal or ignition barrier, is needed often depends on the type of spray foaminsulation that builders use. Many closed cell foam sprays are already sufficiently fire resistant and need no additional barriers. Ultimately, whether or not you need an ignition barrier or thermal barrier varies depending on location and materials. You should check with your local code official to ensure that your insulation work is up to code.

The problem you saw with the closed cell foam pulling away like that is due to the heat of the foam was to hot. It was actually curing out and making foam before it could adhere to the wood. The installer wasn't reading his foam correctly. He should of stopped and turned down the heat on his hose temp. Also installers have to be aware that as the sun rises and the temp in attics rises the subtrates get hotter as well. This will cause the installer to adjust his heat when installing the foam as the temp changes thru out the day.  
The standard prescriptive material that can be used as a thermal barrier is 1/2" gypsum board (a.k.a. drywall or sheetrock). Anything else has to be approved as an 'equivalent thermal barrier' by undergoing tests for temperature transmission and fire integrity. In some cases, however, you need only one test. According to the Spray Polyurethane Foam Alliance (SPFA), "Under specific conditions, the temperature transmission test can be waived if approved by building code authorities on the basis of large-scale fire testing representing actual uses." (See their pdf document, Thermal and Ignition Barriers For The SPF Industry.) Spray Coating Services
We live in middle TN and had our house foamed last year. We noticed recently that some of the foam was shrinking and seperating from the floor joists. We contacted the installer and he informed us that the manufacturer had a problem with a batch of foam during the time frame we had our house sprayed. The contractor wasn't sure if we had the recalled batch installed in our house or not. He said he would check the batch numbers and let us know. He seems like a nice guy promising to do whatever it takes to fix any problems. Do we trust him, however, to be truthful about the batch number? Do we have any options for finding out the information ourselves? I inspected the entire crawl space of the house and noticed approximately (5) areas that were seperating and a couple areas where the foam didn't adhere to the block. Do I assume by it being so infrequent that it is nothing to be concerned about? My concern is the walls that are not capable of being visually inspected because of sheetrock.

Spray foam comes in two flavors, open cell and closed cell, and provides both parts of the building envelope - the insulation and the air barrier. The building envelope should completely surround the conditioned space, and the insulation needs to be in contact with the air barrier. Since spray foam is both insulation and air barrier, proper alignment of insulation and air barrier is guaranteed.
Sta-Kool 800 15-year White Elastomeric Roof Coating is Sta-Kool 800 15-year White Elastomeric Roof Coating is a high quality very flexible white acrylic latex roof coating. Coverage is 50-75 sq. ft. per gallon per coat. Two coatings are recommended. This performance product resists cracking and peeling while offering tremendous durability. This long lasting formula forms and excellent highly ...  More + Product Details Close Spray Coating
I've had concerns with foam in walls with only 2-3" and the resulting air space & convective currents. spray foam for walls is not one of my recommendations to my clients. instead foam sheathing to exterior of walls caulked,taped & sealed. conventional insulation & air tight drywall approach. a better and affordable wall with no extremely long payback like spray foam in walls.  Insulation Spray Coating
Steve: If your spray foam installer leaves the vents open, he will be committing the 2nd of the 4 problems I described above. You will most likely have comfort and efficiency problems. You may well have condensation problems. You will be spending a lot of money on a product that likely won't perform as it should. Don't let him leave the vents open. If the installer you've chosen doesn't understand this, you may want to choose someone else.  Spray Coating Services
Sean, thanks for jumping in and answering John's questions. About choosing the right foam, I intentionally avoided the open cell vs. closed cell foam debate. I did this partly because it's worthy of an article all by itself, but mainly I didn't include it because, despite all the warnings the two sides issue about the other, I've never personally seen a problem caused by using open cell where they should've used closed cell or vice versa. I'm sure things like that happen; I just haven't seen it yet. Coating Services

The problem was that the installer was doing his first spray foam job ever, and the thickness of the insulation varied from zero (visible roof deck) to about 9". Unfortunately, good average thickness doesn't cut it. The coverage needs to be uniform because a lot of heat will go through the under-insulated areas. (See my article on flat or lumpy insulation performance.)
Heat Shield™ EPX–H2O is our #1 high temperature industrial protective insulation coating for equipment. It is a super-powered thermal insulating coating that is also chemical and corrosion resistant and cures within 2 hours to 2 days. Our best in class thermal insulating coatings are proven to solve the most difficult energy efficiency, corrosion, CUI, moisture, and safe touch problems of factories and industry around the world. Spray Coating Services

This product creates a reflective silver finish, thus to help protect roof surfaces and lower roof surface temperature. It uses a low solvent formula, so it dries faster than other roof coatings.This roof coating can be applied by brush, roller or sprayer tip size .040-.061, 1000-1500 psi. We remind you that this product is not suitable for roof repairing, because it can not seal properly.
By heating the full-bodied paint to 60-80 °C, it is possible to apply a thicker coat. Originally the paint was recirculated, but as this caused bodying up, the system was changed to direct heating on line. Hot spraying was also used with Airless and Electrostatic Airless to decrease bounce-back. Two pack materials usually had premix before tip systems using dual pumps.
Mass-produced material is loaded on a conveyor belt where it is fed into one of these flatline machines. Flatline machines are designed to specifically paint material that is less than 4 inches (10 cm) thick and complex in shape, for example a kitchen cabinet door or drawer front. Spray guns are aligned above the material and the guns are in motion in order to hit all the grooves of the material. The guns can be moved in a cycle, circle, or can be moved back and forth in order to apply paint evenly across the material. Flatline systems are typically large and can paint doors, kitchen cabinets, and other plastic or wooden products. Insulation Spray Coating

Hydraulic or air powered airless provide a more uniform pressure control since the paint piston moves at a constant speed except when it changes direction. In most direct drive piston pumps, the piston is crankshaft driven in which the piston will be constantly changing speed. The linear motors of hydraulic or compressed air drive pumps, are more efficient in converting engine power to material power, than crankshaft driven units. All types of paint can be painted by using airless method. Coating Services
If you are looking for the best roof coating, you should try the Heng’s. This product is protective, and can seal vents, air conditioners and more. And it’s budget friendly, we believe you will like it.This roof coating is perfect for RV rubber roof, because it can expand and contract with the roof. It can offer the best protection for the roof in any weather condition. Spray Coating Services
The CWST Thermal Spraying, FW Gartner and Bolts Metallizing business units in AZ, CT, MA, SC and TX apply HVOF, HVAF and plasma thermal spray coatings for flight and industrial gas turbine applications as well as tungsten and chrome carbide wear coatings utilized in Oil & Gas, Mining, Steel Mill and other demanding industrial markets. FW Gartner also provides Laser Cladding and PTA welding services on new and service run parts for components operating in severe service environments. Insulation Spray Coating
Hydraulic and air-powered airless pumps have linear motors that require a hydraulic pump or an air compressor, which can be electric or gasoline powered, although an air compressor is usually diesel powered for mobile use or electric for fixed installations. Some airless units have the hydraulic pump and its motor, built onto the same chassis as the paint pump. Spray Coating
×